Disable Sprinkler System?

Mainstay

Well-Known Member
Reaction score
747
We have relocated our servers for a client into a new room... with a few sprinkler heads covering the entire room.

Of course I want to be safe, but how do you guys handle sprinkler systems? Do you request they be deactivated (the FD has to sign off) or do you use a protective cover on your boxes?

The metal enclosures we use to house the equipment are certainly not water proof =)
 
Good luck getting approval to disable sprinkler heads without a suitable replacement fire suppression tech as well as ventilation. NFPA and building codes will likely dictate that you have exactly what you have.

I would be more inclined to somehow protect the server racks/etc from the water.
 
I would be more inclined to somehow protect the server racks/etc from the water.

Any suggestions? One other tech mentioned he actually installed a SHOWER CURTAIN to protect the servers. If the fire originates from the servers then they will melt the curtain and the sprinklers will still work. If the fire is from somewhere else in the building then the shower curtain may take the brunt of the water.

The FD will likely NOT sign off, I'm sure you are right.
 
First off Sprinklers don't work like in the movies. Only the heads that are tripped go off, not the complete system.

It's not normally up to the Fire Department, it's up to whoever is the Authority Having Jurisdiction (AHJ) which could be the cities/counties planning department or another agency.

You are not going to get an exemption to disable a sprinkler head as the liability is too great. Even if you did your insurance rate would go through the roof.
 
Any suggestions? One other tech mentioned he actually installed a SHOWER CURTAIN to protect the servers.

That would likely work. I've seen basic tarps used before as well.

Mercenary Roadie is largely correct on the Sprinkler heads, too. Only the heads that are directly exposed to heat are going to go off. Usually there is a little red glass vial of glycerin or alcohol wedged in between the heads' water dispersal flare and the 'valve'. The heat causes the liquid inside to expand and break the vial, releasing the valve, hence releasing the water. There are some exceptions to this rule. 1. Don't quote me here, but I believe that Healthcare facilities, schools and a few other 'critical' applications require that all heads go off in a certain 'zone' or floor. 2. Sometimes other heads can accidentally go off in tandem with another because of the water pressure fluctuations during triggering or the pipes were not designed with the proper use of a Water Hammer Arrestor. Usually Water Hammer Arrestors are for stopping issues when turning OFF a valve of some sort.. but I have seen this happen personally as the fire pumps kicked in - with a valve currently open.
 
It's not possible to have other heads go off on certain floors or area by design. Having heads go off because of water hammering is not a problem with correctly designed systems these days.

There is a system that is dry and when the first head goes off it charges the system and then takes a second head to go off before any water is dispersed. The idea behind this it that the Fire Department has a chance to arrive before the second head is triggered.

I know what I am talking about with Fire Sprinklers. My father worked for our County Fire Department and was/is in charge of approving Sprinker designs and I also have two brothers that use to install them.
 
It's not possible to have other heads go off on certain floors or area by design.
Isn't it called a "Deluge System"? When I worked as an electrician they certainly had such systems. This would be mostly in industrial and commercial applications. One such system was at an Ethanol plant I worked on in Chester, VA and the others were at the North Anna nuclear power plant and at the Infineon 200 and 300mm fabs that used to be here in Richmond. I have pulled wire, hooked up fire panels, etc.. so I've been around them a bit, too.

EDIT: Or was it the Pre-Action system? You can certainly zone out areas with a pre-action system, no?
 
First off Sprinklers don't work like in the movies. Only the heads that are tripped go off, not the complete system.

This is what I have to check. The building maintenance guy said otherwise, which was odd to me... because I don't believe they ALL trigger at once. So I wanted confirmation.

The thread wasn't so much about rules and bypassing safety measures, it was to see what other suggestions you guys might have on protecting equipment that ISN'T the culprit. There may be some sort of dry powder dispenser system that we may consider.

If you have a fire bad enough to possibly turn on a sprinkler in your server room then you are already f-cked.

Yup - agreed.
Sometimes other heads can accidentally go off in tandem with another because of the water pressure fluctuations during triggering

This MAY be what the building guy was referring to.... it was a little unclear.

Great feedback - thanks guys!

(I am reading that there isn't an enclosure that you all use / recommend)... Maybe it is time to turn the server room into a tarp city. =)
 
A "Deluge System" is not the same as a Fire Sprinkler system.

Sure it is:
https://en.wikipedia.org/wiki/Fire_sprinkler_system
"Deluge" systems are systems in which all sprinklers connected to the water piping system are open, in that the heat sensing operating element is removed, or specifically designed as such. These systems are used for special hazards where rapid fire spread is a concern, as they provide a simultaneous application of water over the entire hazard. They are sometimes installed in personnel egress paths or building openings to slow travel of fire (e.g. openings in a fire-rated wall).

Water is not present in the piping until the system operates. Because the sprinkler orifices are open, the piping is at atmospheric pressure. To prevent the water supply pressure from forcing water into the piping, a "deluge valve" is used in the water supply connection, which is a mechanically latched valve. It is a non-resetting valve, and stays open once tripped.

Because the heat sensing elements present in the automatic sprinklers have been removed (resulting in open sprinklers), the deluge valve must be opened as signaled by a fire alarm system. The type of fire alarm initiating device is selected mainly based on the hazard (e.g. smoke detectors, heat detectors, or optical flame detectors). The initiation device signals the fire alarm panel, which in turn signals the deluge valve to open. Activation can also be manual, depending on the system goals. Manual activation is usually via an electric or pneumatic fire alarm pull station, which signals the fire alarm panel, which in turn signals the deluge valve to open.

Operation - Activation of a fire alarm initiating device, or a manual pull station, signals the fire alarm panel, which in turn signals the deluge valve to open, allowing water to enter the piping system. Water flows from all sprinklers simultaneously.

But I agree.. only in very specific application would you find this type of system.. so, really, the OP's client's building isn't going to have this most likely.

At the Lake Anna Nuclear Plant they had Deluge systems around some special equipment and materials areas. The part in the Wiki "They are sometimes installed in personnel egress paths or building openings to slow travel of fire (e.g. openings in a fire-rated wall)." was exactly what the plant had, as well.
 
Sure it is:
https://en.wikipedia.org/wiki/Fire_sprinkler_system


But I agree.. only in very specific application would you find this type of system.. so, really, the OP's client's building isn't going to have this most likely.

At the Lake Anna Nuclear Plant they had Deluge systems around some special equipment and materials areas. The part in the Wiki "They are sometimes installed in personnel egress paths or building openings to slow travel of fire (e.g. openings in a fire-rated wall)." was exactly what the plant had, as well.

I tend to not use Wikipedia as a source. I prefer to use the NFPA standards for things like this
 
Do not mess around here. I wouldn't install a shower curtain or anything that can can impede the function of a fire suppression system. You are opening up yourself to a lawsuit.

Just make sure their backup plan is adequate.

THIS

Electrical faults are the number one cause of fires. The most likely place a fire could start would be IN your server room! SO you want to be the guy that instead of just trashing one room your blocked sprinklers allow the entire building to burn down?
 
If you have a fire bad enough to possibly turn on a sprinkler in your server room then you are already f-cked. It really doesn't matter, because either the fire is in your server room or the water is or most likely both.

It's the fact that they can "leak"...(not during a fire, no fire, no heat..)...it's a pressurized water pipe system. They can..leak. Seen there, been there, done that, got the tee shirt.

You can get these plastic domed tops for server cabinets. I have not used them, but I have seen them. White, thin stiff plastic...curved downwards like an umbrella over the server cabinet. If you do some Google-Fu I'm sure you can dig them up...the ones I saw were not home made, they were a designed product.
 